what causes multi-boxes to overheat/cause fires

259 views

How do multi boxes cause fires? Should the circuit breaker trip before it can overheat?

In: 0

6 Answers

Anonymous 0 Comments

I assume you’re talking about extension sockets/leads?

In theory yeah the breaker will trip first in a perfect world. In reality the breaker assumes it’s supplying a single cable, and it doesn’t trip instantly. Two cables sitting next to each other heat up a little bit more than just one. Three or four heat up even more.

Add in that extra extensions cause more volt drop, which can result in end devices drawing more current to compensate.

In the UK it’s pretty normal for the breaker to be rated at 16A or 20A. Several sockets spread throughout the house are on one breaker, and each socket is expected to only take up to 13A max as the end devices are designed for that. But if you’re not a thoughtful user and stick in some extensions suddenly you can very easily exceed the 13A on a single socket, which is bad for that socket but so long as it’s under 16A the breaker won’t necessarily care about it.

There’s nothing wrong with using extension cables or additional sockets. You just need to be thoughtful of what’s being plugged in to it, how long they’re running and how well ventilated (or not) the overall install is.